Thank you for visiting What is the minimum trade size RMC permitted to be installed between two panelboards that are 5 feet apart The RMC will contain four 4. This page is designed to guide you through key points and clear explanations related to the topic at hand. We aim to make your learning experience smooth, insightful, and informative. Dive in and discover the answers you're looking for!

What is the minimum trade size RMC permitted to be installed between two panelboards that are 5 feet apart? The RMC will contain four 4/0 AWG conductors and one 4 AWG ground. All conductors are THHN/THWN.

Answer :

The minimum trade size RMC permitted to be installed, is 4 inches. If the RMC is being used to enclose the conductors and provide physical protection, the minimum trade size required is based on the number and size of the conductors contained within it.

The minimum trade size of rigid metal conduit (RMC) that is permitted to be installed between two panelboards that are 5 feet apart depends on the type of RMC being used and the number and size of the conductors contained within it.

In this case, there are four 4/0 AWG THHN/THWN conductors and one 4 AWG THHN/THWN ground conductor, which requires a minimum trade size of 4 inches according to Table 1 of the NEC.

Therefore, the minimum trade size of RMC that is permitted to be installed between two panelboards that are 5 feet apart, and containing four 4/0 AWG THHN/THWN conductors and one 4 AWG THHN/THWN ground conductor, is 4 inches.

Learn more about RMC, here https://brainly.com/question/28271471

#SPJ4

Thank you for reading the article What is the minimum trade size RMC permitted to be installed between two panelboards that are 5 feet apart The RMC will contain four 4. We hope the information provided is useful and helps you understand this topic better. Feel free to explore more helpful content on our website!